sharan said:How do you wire one common exhaust fan for two separate toilets? Can you connect switches in parallel?
LarryFine said:Then there's the handle-tie requirement if separate circuits are used.
roger3829 said:Why?? If two seperate circuits are used, where does the "handle-tie" come in to play?![]()
480sparky said:210.4(B) .
roger3829 said:210.4(B) is for Multi-wire branch circuits. Multi-wire branch circuits share a neutral. Does not say anything about 2 seperate circuits in the same box requiring a common disconnect.
C3PO said:Look at 210.7(B)
iwire said:To be clear, I don't think it's going to burn the place down, just a NEC issue that is largely ignored. :smile:
mikeames said:Can some one please explain why a standard 3 way wont work??? I guess I don't understand the problem.
mikeames said:Can some one please explain why a standard 3 way wont work??? I guess I don't understand the problem.
steve66 said:The idea is to have one switch in the mens room, and one switch in the womens room. Each switch controls only the lights in the respective room. However, either switch will turn on the same exhaust fan.
Steve