No, the second and last sentence of 2020 NEC 220.60 says "Where a motor is part of the noncoincident load and is not the largest of the noncoincident loads, 125 percent of the motor load shall be used in the calculation if it is the largest motor."
"Used" is not the same as "added". You would use 125 percent instead of 100 percent, i.e. add 25 percent.
As to what those exact words mean, it's a bit unclear to me. ("Used in the calculation" could mean "added to the final total" or it could mean "used in a comparison, not necessarily ending up in the final total.") The scenario the sentence is trying to cover is this one:
You have a feeder supplying among other things a pair of non-coincident loads, say a 60A FLA motor and a 65A non-motor load. Which load is the larger load as far as calculating the required feeder ampacity?
You can't say unless you know the makeup of the other loads on the feeder. If there are no other motor loads on the feeder, then the 60A FLA motor has the larger impact on the feeder ampacity, as when it is included you need to factor it at 125%, and 125% * 60 > 65. But if there is, say, a 100A FLA motor on the feeder, then the 65A non-motor load has the larger impact on the feeder ampacity, as the 60A FLA motor would never get a 125% factor.
Cheers, Wayne