Doing a code review for a chain business, and looking for second opinions if this is a violation or not:
A 20A single pole breaker supplies a small, plug in UPS. The UPS supplies a small panelboard, which has 20A breakers that each supply a single cash register receptacle. I count at least 20 of these receptacles.
Is that a violation of 220.14(I)? Because there are too many receptacles on a single 20A breaker?
Or does that not apply because these are not "general-use" receptacles?
Or does it not apply because the 20A breaker does not directly supply every receptacle on a single branch circuit?