Torque motors and branch circuit sizing

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
It used to be we'd size motor branch circuit based on locked-rotor current for motors that may see high torque during 'stall' scenario, such as a storage tank mixer motor. (Same was true for MOV's, i.e. motor operated valves). According to 430.52 and 240.4(B) however, this is no longer the case...or am I missing something?
 
It used to be we'd size motor branch circuit based on locked-rotor current for motors that may see high torque during 'stall' scenario, such as a storage tank mixer motor. (Same was true for MOV's, i.e. motor operated valves). According to 430.52 and 240.4(B) however, this is no longer the case...or am I missing something?

Locked-rotor current is still used to determine conductor size, overload size and SC/SF protection size for torque motors. See 430.6(B).
 