I would say the old termination should be cut off. By over tightening the wire may have been damaged or compressed to were the proper torque may not be sufficient.
I don't really think the issue is with the conductors.....
Over tightening may have cause the threads to yield. There is no repair for this, replacement only.
Yielding can be difficult to diagnose. It may manifest itself in the form of galling or flaking, but not always. If the yield remained in the ductile state, there may be no way other than precise thread measurements to make an accurate determination.
Never heard of Heli-Coil?Over tightening may have cause the threads to yield. There is no repair for this, replacement only.
I have. They make inserts for repairing all kinds of threads, including spark-plug holes.Never heard of Heli-Coil?
I would say the old termination should be cut off. By over tightening the wire may have been damaged or compressed to were the proper torque may not be sufficient.
That's a great question. One I had not long ago when I asked the electrician to show his lugs were torqued on some switch gear. He had the marks on the lugs indicating they had probably been there but I asked him to check anyway. He ended up being able to get quarter turns on several.
After that I questioned whether or not I should ask to witness torque testing as I was concerned about whether the conductors or the lug terminals might be damaged by this even if they're not tightened beyond their spec???
Never heard of Heli-Coil?
And the inspector will check for this how ?
Not sure how small they make but I've installed hundreds of them down to 10-32 size.I have. They make inserts for repairing all kinds of threads, including spark-plug holes.
And you often will. Torque a conductor today and in a short time you can get movement from a torque wrench.
While we torque everything (and I have since 1976), I would bet 80% of conductors are over tightened and 15% are below specified torque. Of the 5% that are torqued I bet less than 95% are with a calibrated torque wrench. So in my opinion your time is better spent than watching conductors being torqued.
Do you have all the specified torque values?
Do you inspect the torque wrench to verify the settings and calibration?
It's still mind boggling to me how many "electricians" are out in the field practicing that don't own torque tools, wrenches, screwdrivers, etc. In commercial work it’s not AS bad, but in residential the overall quality is WAYYY down.
I've seen pics of what can happen when there are loose connections and since its something that easy enuf to prevent, albeit time consuming during an inspection, I check it.
I do recommend they wait till I get there to torque them but will ask to check even if they're already marked.
Thanks and sorry for potentially hijacking the thread
If the torque values were determined properly, they take into account the thermal cycling that will occur. The installation value will always be higher than the operating value. The trick is getting the specs so that when the connection relaxes over time, there is still a good connection. No matter how much torque is put on a terminal it will always be susceptible to thermal cycling.
(I spent a couple years in my former life as a metallurgical tech at a jet turbine engine parts manufacturer)
To check and re-torque or not should also be part of the design parameters, but we all know that if a tight connection somehow got loose, it won't get any tighter on it's own. Cinching it back down is prudent regardless of what the nomenclature indicates, unless the conductor is damaged, of course.
In the field I see many loose connections. I have never seen a failure due to an electrician tightening loose connections, just failures from people over tightening them or not tightening them enough.
Just some food for thought.....the torque values are calculated to put a certain amount of tensile force on the fastener. Some of that torque will be needed to overcome friction. Here is the question: Will cleaning and lubricating the threads (in order to minimize friction) affect the tensile force? I believe it does. I also believe that the torque specs are calculated with clean and lubricated fasteners and that using those specs on corroded and/or dirty fasteners will result in less tensile force being exerted on the fastener, and result in too loose of a connection.