Re: Torque Survey
Hi pgr; Long time, no see.
I have performed in dependant bench quality tests on push in an wrap around terminations on devices and terminal blocks.
The bum rap for push in connections appears to be when No.#14 could be pushed into No.#12 holes.
I tightened a 12 around a screw, on a receptacle, it took 12 movements to loosing and finally break the wire.
I inserted a 12 in one of the old style receptacles, it took 40 movements to break the wire. The clamp connection was still tight, with shiny copper exposed,
Try this test if in doubt.