Torque Wrench "Crows Foot"
bphgravity
Florida
I recently read this in a UL report:
Q:Reportedly, one manufacture of Rain tight EMT fittings includes a Torque requirement for the installed fitting. How can the torque be verified and enforced in the field?
A:EMT Fittings are Listed under the product category Electrical Metallic Tubing Fittings (FKAV), located on page 33 in the White Book and in UL's Online Certifications Directory at www.ul.com/database. Each of the manufacturers of EMT fittings Listed for rain tight or wet locations achieves their rain tightness by a different method. Therefore it is important to follow the assembly/installation instructions located on the shipping container of the fitting. A ?crows foot? attachment is one method available as a torque wrench attachment for verifying compliance with torque specifications in the field.
Does anyone know what a "crows foot" is and how it works?
Assuming this is the correct thing, it solves the "How to get a wrench around an EMT fitting" problem so you can attach a torque wrench to the fitting.
Yes but remember that because you have just moved the center of rotation you will now need to correct or adjust the values you use when tightening because of the longer arm applying the torque, or am I wrong about this?
If you install the crow's foot on the wrench so it increases the effective length, then you must increase the measured torque by the ratio of the new length to the old length. You won't be far off if you add 10% to the measured torque.
If you install the crow's foot so the toes point in the direction you are pulling, then there is no change in length and you don't need to make any correction.
The length of the moment arm is different, because you aren't turning the torque wrench output shaft about the center of the fitting. However, your new center of rotation is also moved out, so it's back to r X F. Since you are no longer coaxial to the fitting, the net result is about unity, meaning "don't use a fudge factor". You're gaining torque because of the slightly longer moment arm, but you're losing torque between the square socket and the center of the jaws because of the different centers of rotation. The crow's foot rotates about the fitting, and the torque wrench rotates about the square hole in the crow's foot. Studying the two motions would be an interesting study in Coriolis acceleration, while they're moving :)
Dan
Do they make a 2.5" or 3" crow's foot for large EMT? I doubt it. The idea of using a torque wrench on an EMT fitting is ridiculous to begin with. A more appropriate method would be for the manufacturer to design the fitting so that it can be field installed wrench tight with a pair of pump pliers. This is how they are installed on a daily basis.
Dunno. It seems somewhat likely that we may have to resort to the "spot torque" methodology.
Are you familiar with that spec? The way I remember it, it has something to do with the spots you see while you are grunting....
One of my electricians is known by his peers as "Torque". He has the distinction of being able to connect any pair of threaded connectors irreversibly unless you accept destruction in the act of disassembly.
Dan
Dan
No Dan. The torque wrench applies the measured torque at the square drive of the wrench where it connects to the crow's foot, and it applies a force to the drive point of the crow's foot equal to the force that you pull on the wrench handle. The torque corresponding to the product of that force, times the distance from the crowfoot drive to the center of EMT, is added to the torque measured by the torque wrench.
It will be clear if you draw the force and moment diagram for the point where the torque wrench applies the torque, and then use those forces to calculate the torque applied to the nut.
Here is my invention for you guys who need a tool for measuring torque when torquing up big EMT nuts:
Get a pipe wrench and cut off the handle. Weld something with a 1/2" female square drive to it. The applied torque is the measured torque with the wrench times the ratio of the new total length to the old length from drive point to pivot in the torque wrench handle.
Torque = (measured torque) x (extension + original length) / original length
They day we start torquing EMT nuts is the day I'll retire. I'm all for following instructions, but a fella's gotta draw the line someplace.
All right, I'm trying to follow you on this one, Bob. Let's say you've got your crow's foot wrench at the nine o'clock position, as viewed from above, on a nut with a right hand thread. So, your square hole for the torque wrench is at 180 degrees on the cartesian coordinate system I have arbitrarily defined in this system as positive X right, positive Y up. There are several situations I can see on this one.
Assume that r1 is by definition the mean distance from the square drive of the crow's foot to the center of the crow's foot jaw (i.e. the conduit).
Assume that r2 is the length of the torque wrench handle from the center of the square drive to the effective position of the electrician's hand.
Assume the electrician always provides force normal to the line defined by r2.
Situation one: Wrench handle at zero degrees in my defined plane - torque is diminished by r2-r1.
Situation two: Wrench handle at 180 degrees - torque is increased by r2+r1
Any time the variation in torque will be defined by (r1-r2) * the cosine of the angle subtended between r1 and r2.
When the wrench is orthogonal to either of these two conditions (cos theda = 0), the resultant torque on the object nut is exactly equal to the applied torque. The applied torque is r times F times sin [angle between r and F], always. r is the distance from the center of rotation of the fastener you're twisting to the effective point of where you're making the twisting motion. F is the force you're applying to make something happen. sin theda is the sine of the angle between the radial line passing through the center of "desired" rotation and the vector in line with the force you are applying.
Conclusion: I'm right on only two unique positions out of an infinite number of possibilities. Of the rest of the possibilities, half of the time I'm high, and half of the time I'm low. To correct my original statement, make sure you have the handle of the torque wrench at a 90 degree angle to the line from the middle of the square socket on the crow's foot to the center of the conduit, and you'll not have to compensate for any crow's foot geometry ;-)
An exaggeration to prove the point goes like this. Let's say the crow's foot is of infinite length from the center of the jaws to the center of the square drive. Question: If you apply force on a 3 foot wrench at a 90 degree angle to the line from the center of the jaw to the center of the square drive on that, how much torque are you applying to the nut?
Answer: None. You'll pull the crow's foot straight off the nut.
If you put your wrench handle in line with that infinitely long axis, any force you apply orthogonally will twist the nut right off or on. I think the math still works with realistic dimensions. Thanks for pointing out the error; I only considered the orthogonal axis situation.
Yes, you're right. Sorta:) ||r X F|| is by definition r * F * sin theta, right?
Marc, only "spot torque" the biggens.
Edited 09 Nov 2006 - 2239 - Of course, the infinitely long linkage would have to be massless or you wouldn't be able to budge it...
I'm ROTHFLMAO on this one!!
I brought this up to a UL rep at an IAEI meeting. At least a year ago when these things were first touted as being suitable as raintight.The fact that Steel City fittings include a torque setting in their instructions. I asked him in a respectfull yet joking way "Are you Nuts!!" How do you expect this this to be realistically followed in the everyday world??
He really had no answer. This was how the manufacturer submitted it for evaluation.
Just goes to show that a lot of people are out of touch with reality.
Good morning, all. I did a really crappy explanation in post #10. I'd like to take another stab at it if nobody minds. (suspenseful pause follows)
Let's say the electrician's torque wrench is made such that he/she can pull on it at exactly one foot from the square drive. If the drive is directly on the fastener, meaning no crow's foot, then every pound of force the electrician applies at 90 degrees to the wrench handle is one foot-pound of torque on the fastener. For you purists, the fastener is a perfect fastener. (har-har!) Let the line through the wrench from the center of the square drive out through the end of the handle be the X axis. At the point the torque is applied, X=1.0 foot.
Now introduce the crow's foot. Place the crow's foot on the torque wrench so that the jaws point left 90 degrees from the handle of the torque wrench. Let the line passing from the center of the square drive hole through the center of the jaws be the Y axis.
Let the center of the jaws be the origin in our coordinate system.
Now place the crow's foot on the right hand side of the fastener you are tightening. (assuming the perfect fastener is a right-hand thread here)
Let's say the distance from the center of the square drive to the center of the jaws on the crow's foot is 12 inches, to make the calculation a little more straightforward. (Y = 1.0 foot)
The force applied to the torque wrench is still one pound., and is still applied at a right angle to the wrench handle. Therefore the applied force is completely parallel to the Y axis.
The length of the moment arm r between the electrician's hand is sqrt( X^2 + Y^2), which becomes sqrt(2) foot. Yes, it's a longer arm. However, torque is the vector cross-product of the moment arm and the force applied. Its magnitude is given by ||T|| = r * F * sin (theta). In the current model theta is the angle between the Y-axis and the line connecting the center of the fastener with the point on the wrench our electrician is applying force.
sin (theta) = X/r = 1.0/sqrt(2) = sqrt(2)/2.
Substituting in the earlier equation, T = sqrt(2) * F * sqrt(2)/2. This reduces to T = 1.0 * F in this case.
It may be shown that for any crow's foot effective length Y, that as long as the crow's foot is perpendicular to the torque wrench handle, you can ignore it.
Gotta put my pants on and go to work now.
Dan
"It may be shown that for any crow's foot effective length Y, that as long as the crow's foot is perpendicular to the torque wrench handle, you can ignore it." Dan
That is what I said way back in Post 4, without any need for vector algebra! See quote below.
"If you install the crow's foot on the wrench so it increases the effective length, then you must increase the measured torque by the ratio of the new length to the old length. You won't be far off if you add 10% to the measured torque."
"If you install the crow's foot so the toes point in the direction you are pulling, then there is no change in length and you don't need to make any correction."
Hi, Bob. Right you were, and still are. I wasn't debating your post, I was agreeing with it. I always put the jaws that way myself, and I didn't stop to think that maybe not everybody else did. So, off to the chalkboard I went. It didn't look so in hindsight; I thought I was filling in the blanks. Oops!
Dan
Give the facts that type "W" conductors would be used, condensation is inevitable, and the raceway has to be arraigned to drain, what is the point of the raintight fittings in the first place?
Roger
I disagree -- I think the new length becomes the hypotenuse of the triangle, but I'm head hurts too much to do the vector math.
(No, really -- I have a headache.)