For load centers lugs what range of torque wrench should be used.
looking to get a wrench but not sure the range of Inch pounds I should be looking for.
Infinity
Do you have a seperate wrench for inch pounds?
Infinity
I convert.
12 in/lbs = 1 ft/lb
Even if you use a torque screwdriver, if the setting is in the 20 - 25 in/lb range that feels like it will break your wrist if you do it too many times, and I can see why carpel tunnel syndrome is popular in people the electrical trade.Yes, we do the simple conversion for lugs listed in inch pounds. Slotted screws below 10 ft pounds usually get torqued with one of these:
We do use micro torque wrenches for things like battery jars on UPS systems where the torque values are very low.