Let's say I have 3 RTU units at 208/3P
RTU #1: 48A MCA, 60A MOCP
RTU #2: 30A MCA, 40 MOCP
RTU #3: 22A MCA, 30 MOCP
Based on 220.50, I need to take 125% of the largest motor.
But do I use the 48 MCA or do I need to find the FLA.
But doesn't the MCA already calculate 125% of the largest load when sizing the MCA from the manufacturer?
Also, after finding the largest load, what load do I use when I calculate RTU #2 and RTU #3 for the load calculation at 100%?
Do I use the 30A and 22A of the MCA or FLA?
Also if there is refrigeration (Walk in) equipment, do I use 100% load if it's not the largest load?
Or can I consider the Walk-in as a Kitchen Equipment Load and use Table 220.56?
RTU #1: 48A MCA, 60A MOCP
RTU #2: 30A MCA, 40 MOCP
RTU #3: 22A MCA, 30 MOCP
Based on 220.50, I need to take 125% of the largest motor.
But do I use the 48 MCA or do I need to find the FLA.
But doesn't the MCA already calculate 125% of the largest load when sizing the MCA from the manufacturer?
Also, after finding the largest load, what load do I use when I calculate RTU #2 and RTU #3 for the load calculation at 100%?
Do I use the 30A and 22A of the MCA or FLA?
Also if there is refrigeration (Walk in) equipment, do I use 100% load if it's not the largest load?
Or can I consider the Walk-in as a Kitchen Equipment Load and use Table 220.56?