BatmanisWatching1987
Senior Member
- Location
- NJ
- Occupation
- Jr. EE
The current electrical service at the store is 200 AMP/208V/3P
Here is a list of circuits
12 Styling Chairs, which each requires 2 dedicated circuits = (12*2*1500)= 36kW
3 Hair Dryer Station with 1 dedicated circuit each = 4.5kW
3 Shampoo Station with 1 dedicated circuit each = 1.5kW
18kW Electric Hot Water Heater = 18kW
7.5 Ton RTU (60 AMP/208V/3P) = 21.6kW
What is the typical load do you show for a dedicated circuit for a styling station and hair dryer station?
I usually show 1500W for each and 500W for the Shampoo Station.
I got a total of 81.6 kW, which is about 226 AMP.
Is there a demand factor I can use for a Barber/Salon to reduce the electrical load of the Receptacles, Hot Water Heater or RTU?
Here is a list of circuits
12 Styling Chairs, which each requires 2 dedicated circuits = (12*2*1500)= 36kW
3 Hair Dryer Station with 1 dedicated circuit each = 4.5kW
3 Shampoo Station with 1 dedicated circuit each = 1.5kW
18kW Electric Hot Water Heater = 18kW
7.5 Ton RTU (60 AMP/208V/3P) = 21.6kW
What is the typical load do you show for a dedicated circuit for a styling station and hair dryer station?
I usually show 1500W for each and 500W for the Shampoo Station.
I got a total of 81.6 kW, which is about 226 AMP.
Is there a demand factor I can use for a Barber/Salon to reduce the electrical load of the Receptacles, Hot Water Heater or RTU?