Touch potential calculations/test

Status
Not open for further replies.

lielec11

Senior Member
Location
Charlotte, NC
Anyone know what type of calculations are involved for a touch potential test? Client of mine had a requirement come across their desk and I've never performed anything like that. Now I am curious as to what is actually involved in the calculations and field tests in determining the touch voltages.
 

Julius Right

Senior Member
Occupation
Electrical Engineer Power Station Physical Design Retired
Earthing of power installations exceeding 1 kV a.c,
BS EN 50522/2010 or IEC/CENELEC EN 50522/2010(E) Annex H.
For indoor or outdoor installations.[ See ch.1 Scope for what is considered by this standard as electrical power installation.]
For substation outdoor installations:
IEEE Std 80-2013
IEEE Guide for Safety in AC Substation Grounding
19.2 Field survey of potential contours and touch and step voltages
 

Sahib

Senior Member
Location
India
I wonder whether NEC requires any touch potential calculation/test. I believe it does not.
 
Last edited:

lielec11

Senior Member
Location
Charlotte, NC
I don't believe so but it was listed as a requirement from the local utility company for this specific project. To be honest it's the first I've seen for a traditional 15kV-480V step-down indoor switchgear.
 

Sahib

Senior Member
Location
India
Then the local utility company may be approached for a model touch potential calculation and test procedure because it is their requirement.
 