silurian
Member
- Location
- Northern Wisconsin
I was asked to give an estimate for out local Town Park Shower building. It has a 400 amp Sq D QO load center with a 400 amp meter socket, back to back. No disconnect in between. Two sets of paralleled 4/0 4/0 2/0 feed the panel from the meter socket. Their main concern is having the well, which is protected at 70 amps, and the lights in the shower area on the generator. Also, the park office is connected to the same building, so the town foreman thought lights and the receptacles in the office would be good as well. Clearly, the requested generator load is not 400 amps, nor is the load of the entire building. Besides the well, it is LED lighting and general purpose receptacles. However, there is no room for a transfer switch inside the utility room. So the only option is an exterior "whole load" transfer switch. So, my question is: Is is code compliant to control and power one just one set of the paralleled conductors with the transfer switch and generator as long as the other set passes through the switch as well so the paralleled conductors stay together.