TR receptacles in hallways of multi family dwellings.

Status
Not open for further replies.
Start at 406.12. That says that for a dwelling unit (and that would include the multifamily ones), all receptacles required by 210.52 shall be TR. 210.52(H) requires at least one receptacle in a hallway. I don't see lobbies mentioned in 210.52. But a lobby might be treated like a foyer, as mentioned in 210.52(I).
 
Start at 406.12. That says that for a dwelling unit (and that would include the multifamily ones), all receptacles required by 210.52 shall be TR. 210.52(H) requires at least one receptacle in a hallway. I don't see lobbies mentioned in 210.52. But a lobby might be treated like a foyer, as mentioned in 210.52(I).

Much thanks:thumbsup:
 