Common areas, lobbies, hallways etc. require TR receptacles ??
Ref. please.
Ref. please.
No reference, but why wouldn't you? The time to look for and stock Non TR isn't worth it.Common areas, lobbies, hallways etc. require TR receptacles ??
Ref. please.
Start at 406.12. That says that for a dwelling unit (and that would include the multifamily ones), all receptacles required by 210.52 shall be TR. 210.52(H) requires at least one receptacle in a hallway. I don't see lobbies mentioned in 210.52. But a lobby might be treated like a foyer, as mentioned in 210.52(I).