yes.
all receptacles that are required per 210.52 must be TR type.
 
Yes, GFCI protection also. 210.8.

406.11 Tamper-Resistant Receptacles in Dwelling
Units. In all areas specified in 210.52, all 125-volt, 15-
and 20-ampere receptacles shall be listed tamperresistant
receptacles.

210.52(G) Basements and Garages. For a one-family dwelling,
the following provisions shall apply:
(1) At least one receptacle outlet, in addition to those for
specific equipment, shall be installed in each basement,
in each attached garage, and in each detached garage
with electric power.

too slow again.
 
Last edited: