hbiss
EC, New York NEC: 2017
- Little Falls, New York NEC: 2017
- EC
Does the Code allow track lighting to be controlled by dimmers? Although I have done it I have never been sure if it is correct.
404.14(E) says:
General-use dimmer switches shall be used only to control permanently installed incandescent luminaires (lighting fixtures) unless listed for the control of other loads and installed accordingly.
410.101(A) says:
Lighting Track.
Lighting track shall be permanently installed and permanently connected to a branch circuit. Only lighting track fittings shall be installed on lighting track. Lighting track shall not be equipped with general purpose receptacles.
Question is are the heads considered part of the track assembly or not? I say they are not but there are lighting manufacturers who say their heads can be used with a dimmer.
I wouldn't consider the track to be any different than receptacles on a wall. The customer is free to connect many different types of heads, some of which are fluorescent, LV with transformers and electronic transformers and HID.
-Hal
404.14(E) says:
410.101(A) says:
Lighting Track.
-Hal