A lighting designer wants me to draw up the electrical drawings for the following: a few hundred feet of track lighting connecting to a current limiting panel that has small circuit breakers... not sure how small they are, but i'm assuming around 3 or 4 amps.
I'm not entirely sure how to put this together. Is this correct?:
Design the feeder / main breaker that feeds the current limiting panel according to section 220.43(B), which is 75VA per foot. So I'll take the total feet of the track and multiply by 75 VA, and then multiply by 1.25 since it's a continuous load. Next size up would give me the breaker / feeder size.
Then I would have the individual tracks connecting to the small breakers on the current limiting panel. The breaker size for each track / circuit would be based on the actual bulb wattage divided by the voltage (120).
Do I have this correct?
I'm not entirely sure how to put this together. Is this correct?:
Design the feeder / main breaker that feeds the current limiting panel according to section 220.43(B), which is 75VA per foot. So I'll take the total feet of the track and multiply by 75 VA, and then multiply by 1.25 since it's a continuous load. Next size up would give me the breaker / feeder size.
Then I would have the individual tracks connecting to the small breakers on the current limiting panel. The breaker size for each track / circuit would be based on the actual bulb wattage divided by the voltage (120).
Do I have this correct?