Article 220.43(B) addresses track lighting loads for services but not for branch circuit loading. Article 410.151(B) does address branch circuits but only mentions the connected load on lighting track shall not exceed the rating of the track light. But how do you actually determine how much load you can put on one branch circuit? Im sure it is permissible to use 220.43 but it doesen't explicitly say in 410 that you should or have to.
So if you have 100 feet of 120v single circuit track light, how many 20A circuits does this require?
According to article 220 at the service level this would be 100 feet * 75va/ft = 7500 va.
So if you have 100 feet of 120v single circuit track light, how many 20A circuits does this require?
According to article 220 at the service level this would be 100 feet * 75va/ft = 7500 va.