I am working on a track lighting calculation I wanted to make sure I had it right.A lighting plan shows 58.5 linear ft of single track lighting for a small department store.Neither the quantity of track lighting nor the lamp is specified.What is the minimum calculated load associated with the track lighting that must be added to the feeder supplying the store? 58.5/2=29.1times 150va=436.5va so the answer is 436.5 if I did it correctly,thanks for help
 

topgone

Senior Member
I am working on a track lighting calculation I wanted to make sure I had it right.A lighting plan shows 58.5 linear ft of single track lighting for a small department store.Neither the quantity of track lighting nor the lamp is specified.What is the minimum calculated load associated with the track lighting that must be added to the feeder supplying the store? 58.5/2=29.1times 150va=436.5va so the answer is 436.5 if I did it correctly,thanks for help
Please check your math. 29.1 x 150 = 4365VA.
 