Yes I did But that has to do with feeder calculation not branch circuit. I Know that you are trying to help and I am greatfull. Just when you think the code has answered your question there seems to always be another part that tells you differently. Has any one else ran into this problem
The FPN is not for feeder calculations. It is saying that the length of track is not limited by the calculation for the load of the branch cir. The FPN states that this does not mean the lengh of track or the number of fixtures are limited. The FPN was put in to clarify.
2005 NEC said:
art. 410.101(B) Connected Load. The connected load on lighting track shall not exceed the rating of the track. Lighting track shall be supplied by a branch circuit having a rating not more than that of the track.
If you look at a Halo track it states that the
Solid copper bus bars [cross section equivalent to #12 AWG wire].
Thus a #12 20 amp circuit is all that is permitted. This protects the track should someone connect a load beyond it's capacity. It does not limit the length of the track. I can run 100' of track and have 5 fixtures on it with 100 watt bulbs and there is no issue.
Ask the inspector what he is concerned about if the track is rated 20 amps and you are protecting the circuit with a 20 amp CB and #12 wire. Or 15 amps and #14 wire for that matter. If the owner adds too many tracks the cir. will blow.
I will say this, IMO, if the track heads can take a 150 watt bulb and you put in 50 watt bulbs you would still need to calculate the circuit based on the 150 watt lamps.
Also ask the inspector to show you where the track is limited in length. He will not be able to.