ryan_618
Senior Member
- Location
- Salt Lake City, Utah
Have I been mis-interpreting this? I was just reading in my 99' NEC (don't have 02' here now) about track lighting, specifically 220-12(b). I just realized that this is under the article for feeders and services.
The scope of article 220 is: "This article provides requirements for computing branch-circuit, feeder, and service loads".
With that in mind, I have asked on plan reviews to accomodate 150 Volt-amps for every two feet of track on the branch circuit !!! Is this only for the feeder/service calculations? If so, is there an errata to it or was it changed in the 2002? I really hope I haven't been calling this incorrectly!
The scope of article 220 is: "This article provides requirements for computing branch-circuit, feeder, and service loads".
With that in mind, I have asked on plan reviews to accomodate 150 Volt-amps for every two feet of track on the branch circuit !!! Is this only for the feeder/service calculations? If so, is there an errata to it or was it changed in the 2002? I really hope I haven't been calling this incorrectly!