Greetings,
I have drawings for a solar system for a commercial system - 3 phase wye.
I started in section 690 of the code -
calculated the maximum current = 79 Amps - (2 Fronius Inverters w/ max current = 31.6 amps:
(31.6+31.6)*1.25)= 79 amps
Then Section 690 tells me to go to section 240 for conductor sizing but I don't see within section 240 a place specifying conductors going up to and beyond this current.
How can I tell from the NEC code what conductor size to use for 79 amps in a solar arrangement?
Also the system has a 40 amp breaker panel with 2 Fronius Solar inverters feeding the panel. The maxium output current from 1 inverter is 31.6 amps.
Is this arrangement ok?
Thanks
Sparky_
I have drawings for a solar system for a commercial system - 3 phase wye.
I started in section 690 of the code -
calculated the maximum current = 79 Amps - (2 Fronius Inverters w/ max current = 31.6 amps:
(31.6+31.6)*1.25)= 79 amps
Then Section 690 tells me to go to section 240 for conductor sizing but I don't see within section 240 a place specifying conductors going up to and beyond this current.
How can I tell from the NEC code what conductor size to use for 79 amps in a solar arrangement?
Also the system has a 40 amp breaker panel with 2 Fronius Solar inverters feeding the panel. The maxium output current from 1 inverter is 31.6 amps.
Is this arrangement ok?
Thanks
Sparky_