QUESTION: TRACT LIGHTING USED FOR GENERAL/RETAIL LIGHTING - SIZING FEEDER/SERVICE AND SIZING BRANCH CIRCUITS.
SEEKING CONFIRMATION OF CODE
BASED ON ART. 220.12, THE SERVICE AND FEEDER TO PANEL SUPPLYING POWER TO TRACK LIGHTING SYSTEM SHOULD BE SIZED 150va PER 2' OF TRACK.
HOWEVER, BRANCH CIRCUIT CAN BE SIZED BASED ON ACTUAL FIXTURE COUNT INSTALLED ON TRACK. (i.e. 30' OF TRACK HAS 6 - 70W SPOTS = 420W LOAD NOT 15X150VA OR 2250VA OF LOAD.) THE 2250VA WOULD BE USED FOR SIZING PANEL AND FEEDER/SERVICE. 420W WOULD BE USED FOR SIZING BRANCH CIRCUIT.
IS THIS THE CORRECT INTERPRETATION?