I got a call from a guy that was working under a trailer house and was getting shocked from the metal frame of the trailer home.
What could cause this?
What could cause this?
How was he getting shocked, from the trailer to the ground? Could be many things, one the trailer isn't grounded and there is a fault in the wiring somewhere energizing all of the metal parts.
Take a look at NEC 552.56(A). All exposed metal parts including frames have to be bonded to the grounding terminals or enclosure of the distribution panelboard. If a hot wire is touching that frame then the OCPD should've tripped.
Can these two comments be reconciled? Would lack of ground cause the OCPD to not function?
I agree with you.If the trailer frame is not grounded/bonded and becomes energized, how would the OCPD trip? There would not be any current flow.
Hard to interpret your questions using only the word "ground" to mean several aspects of a properly wired system, but...
Neutral is typically bonded the grounding system at or near the power source. The grounding system has equipment grounding, non-current-carrying metallic parts grounding, and also earth grounding (the grounding electrode system, GES). Losing any part of this grounding system will still allow over current devices to trip as long as the remaining paths provide sufficiently low enough impedance for the fault current to return to the source.
If the trailer frame is not grounded/bonded and becomes energized, how would the OCPD trip? There would not be any current flow.
Yes... but it may not be a grounding issue.Can these two comments be reconciled? Would lack of ground cause the OCPD to not function?
Yes... but it may not be a grounding issue.
There is a fault somewhere, without a doubt. Even if the frame is grounded, the fault may be resistive, thus not allowing enough current to trip the breaker.
The bonding jumper connection to the frame, if present (usually installed by the manufacturer, though), may be corroded and resistive rather than solidly connected.
If the person getting shocked is touching the frame at a point remote to where it is grounded and much closer to where the fault is occuring, he is completing one path back to the source. It does not take much current to get shocked.