I have 3 ph 480V primary. I need to get 400A on the secondary (120v - 208v)>

Can someone tell me the size of the transformer and what amperage my primary should be?

Thanks in advance, I'm just checking myself.
I came up with Primary amps at 175 and the transformer at 112kva.
 

jatrottpe

Member
Location
NJ
400A per phase secondary
400A * 208V * 1.732 = 144.102kva ~ 150kva transformer

Primary
144102 / (480 * 1.732) = 173a

150000 / (480 * 1.732 ) = 180a
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I agree with jatrottpe's math. Please note, however, that the values of 400 (secondary) and 180 (primary) are the transformer's approximate current ratings, not the ratings of the associated overcurrent protection device.
 