tranformer supply circuit breaker size in the sourece , the minimum

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
What is minimum size breaker in the source (A panel board) for 45 kva-3ph.-tranformer .
the subject, the load is lights/ receptacles through a sub panel ( total 20,000 VA).

Also, what minimum size fuses in primary side, adjusnt mounted manual disconnect switch
 
The NEC does not set a minimum size for the primay OCPD. We need to know the voltages to make any OCPD sizing calculation. You can't go too small or the OCPD will open on the transformer inrush current.
 