Re: Tranformer Testing
If you are asking about theory, then the most common formula that is related to this question is that power equals (voltage squared) divided by resistance. That means that resistance will equal (voltage squared) divided by power.
R = (480 x 480) / (150) = 1536 ohms (as seen by the primary)
R = (120 x 120) / (150) = 96 ohms (as seen by the secondary)
Please note that the actual numerical values are approximate, simply because the 150VA, 480V, and 120V are ?nominal values.? In order to determine the actual value of resistance for a specific coil, you need to use the test equipment that Bennie has described.