a three phase 480v 45 Kva transformer that the prints show to be floor
mounted--is the enclosure rated nema 9--could you raise the transformer up
to 18" above the ground and have the area around it ventilated--or is ventilation even needed if the transformer is above 18'--is it a general
practice to set the transformer on the floor and have it encapsulated?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Lawrence,
Look at 501.100(B). Standard transformers are permitted to be used in Class I, Division 2 areas.
Don
 

rbalex

Moderator
Staff member
Location
Mission Viejo, CA
Occupation
Professional Electrical Engineer
I am making the assumption that the classiciation is Class I , Division 2. If that is correct, see [NEC 2005] Section 500.100(B).
 