Is there a formula to calculate inrush current and duration for transformers?
Thanks
Thanks
Not really.Is there a formula to calculate inrush current and duration for transformers?
Thanks
Of course there is!
I'd present it ...
Estimate is 12 x FLA.
What I'm trying to determine is if there is any chance I could energize a 300kva 480delta 208y/120 tranny with a 100A Seimens BQD breaker.
#1: The primary (assuming step-down) current of a 300kVA transformer is going to be 360A, without even BEGINNING to discuss inrush!
#2: If, by chance, you have a typo and this is a 30kVA transformer, but the application is in a true 480V delta system, then you cannot use the BQD at all, it is a "slash rated" breaker and can only be used in 480/277V systems.
What I'm trying to determine is if there is any chance I could energize a 300kva 480delta 208y/120 tranny with a 100A Seimens BQD breaker.
What is the FLA of a 300kva transformer at 480v? 360a? If the inrush were to be even as low as 10x the FLA it would be 3600? Now how does this we work out with a breaker with a 1200a instantaneous trip?
I have seen 75kVA 480V-208Y/120V units blow fuses when unloaded, and the same fuses hold when there was a load.If there is no load on the secondary the inrush is the same???
I have seen 75kVA 480V-208Y/120V units blow fuses when unloaded, and the same fuses hold when there was a load.
Got a theory behind that?
Got a theory behind that?
If there is no load on the secondary the inrush is the same???