Roger Crawford
New member
I have a system that has a generator with a standby transfer switch and a life safety transfer switch. Both transfer switches are 3-pole, so not a separately derived system. The life safety transfer switch feeds a 4-wire + ground panelboard, and the standby transfer switch feeds only a 3-wire 480 volt 3-phase panelboard. The question is, with a non-seperately derived system is a neutral conductor required to be brought to the transfer switch from both the generator and normal power feed? If the transfer switch is in the standby position and a phase-ground fault ocurs how will the breaker at the generator see enough current to trip, without the neutrals tied together?