I’m in need of some help. I have installed a battery back-up system. Instead of pulling specific circuits to the critical load panel I installed an automatic transfer switch so that when utility power goes out it would transfer the load to the critical load panel. When I went to test the system by turning off the main breaker the ATS never transferred from utility to the critical load (or the terminals where the generator wires would normally land). There was voltage on the critical load side of the switch where normally the generator wires hook up. I am using a Siemens 100 amp transfer switch (basically identical to a Generac). Read online that Siemens ATS will iniatiate from the gen via signal wire on the N1 and N2 (utility sensing) terminals. Since I don’t have a gen what can I do? Is there a way around it? I’m thinking a contactor or relay of some sort? The ATS will operate manually once I turn off main breaker and automatically transfer back when utility is restored.