Hey guys, my client wants me to go Indiana (12 hours away) to finish a 400 kw generator install. Just trying to get a rough game plan. As you can see, it's a 2000A Siemens switchboard with a Pringle switch. Anyone happen to be familiar with these Siemens switchboards? Questions:
1. Is there metering below the service disconnect ? Doesn't seem like there's much room under there. There is an instrument meter on the exterior so it's definitely not metered at the transformer spades.
2. Any idea what fuse type this is likely to have? Service is 120/208 I suspect this is grossly oversized and may down grade it to make it easier.
3. Transfer switch is not service rated. Would have to intercept load side bussing. Can't think of anything else to do besides remove bussing between the load side of the switch and the distribution section and put lugs on. Seems like this isn't an uncommon thing, how is this typically done? Do manufacturers offer kits for this?
Thanks
1. Is there metering below the service disconnect ? Doesn't seem like there's much room under there. There is an instrument meter on the exterior so it's definitely not metered at the transformer spades.
2. Any idea what fuse type this is likely to have? Service is 120/208 I suspect this is grossly oversized and may down grade it to make it easier.
3. Transfer switch is not service rated. Would have to intercept load side bussing. Can't think of anything else to do besides remove bussing between the load side of the switch and the distribution section and put lugs on. Seems like this isn't an uncommon thing, how is this typically done? Do manufacturers offer kits for this?