We are having situations where the installer is taking the service conductors, after the meter in a combination meter main service panel (main bus with combined neutral/equipment grounds) condition and routing the conductors to an ATS. They then run the conductors back to the "main service panel" (the location in which the service entrance conductors originated before and after the meter with the main bussing) with no main disconnect in this panel. The installer is then attempting to claim the ATS is the main service disconnect and is bonding the grounds/neutrals with the jumper wire.
I am finding this to be a direct violation of NEC (CEC in CA) of 250.142 (1) for the required bonding of the grounded conductor. Any thoughts or feedback on this would be appreciated.