This seems to be improperly installed. this is what I see, please correct me if I'm wrong or add to the list.
not SE rated
nipple not bonded correctly
SEU should replaced with SER
service grounding still in main panel
Service entrance conductor spliced
no bushing on generator conductor conduit
This is not my install. I was called by my customer to install a generator for him at the same price as this one which was installed at his friends house. No permit and I beleive installed on a Sunday morning for $7000.00. Generator is a 20 kw natural gas. The installation included gas piping as well. one other item i don't know the answer to is the exhaust end of the genny is appx 2 feet from the gas meter. Problem ?
not SE rated
nipple not bonded correctly
SEU should replaced with SER
service grounding still in main panel
Service entrance conductor spliced
no bushing on generator conductor conduit
This is not my install. I was called by my customer to install a generator for him at the same price as this one which was installed at his friends house. No permit and I beleive installed on a Sunday morning for $7000.00. Generator is a 20 kw natural gas. The installation included gas piping as well. one other item i don't know the answer to is the exhaust end of the genny is appx 2 feet from the gas meter. Problem ?