Transfer switch location

Status
Not open for further replies.

ryan_618

Senior Member
I seem to remember an allowance of having a transfer switch located on the supply side of the service disconnect, if the transfer switch is listed as service equipment. I see no such allowance in 230.82, however.

Does anyone know of an exception to this somewhere?
 

Duuuuug

Member
Re: Transfer switch location

ryan,
Can't remember where in the code, but I seem to remember that the ATS must be located immediately adjacent to the main breaker
 

ryan_618

Senior Member
Re: Transfer switch location

Bob is right. It is not allowed before the service equipment (230.82) unless it is the service equipment, in which case 230.82 is irrelevent.
 
Status
Not open for further replies.
Top