Alex1995
New User
- Location
- Pennsylvania
- Occupation
- Electrician
Customer had a 100A 240v 20kw generac with an automatic transfer switch. Verified that the voltage was 240v phase to phase, and 120v phase to neutral and phase to ground. The load wasn’t transferring to emergency, so I swapped out the whole ATS. Still not transferring properly. It will transfer to emergency manually, just not automatically. When power is restored, it senses and the generator transfers back to normal automatically and goes into cool down.
Started looking more in depth and saw I was only getting 2.5vdc from the 12vdc terminal(193) to (0) ground. I was also getting 0v from 193 to to transfer(23). Then I shut the breaker off to try and transfer the load, the generator started, and I got the same readings. If I pull the 12vdc wire off of the SACM board, it then reads 12vdc as it should. As soon as I put it back on the SACM board it drops back to 2.5vdc.
Thought there may have been a short in the wires so I toned them all to make sure I had continuity and also separated them to make sure I was getting no continuity on wires unintentionally. Then thought maybe something was wrong with the SACM so I swapped the whole board and it continued to do the same thing. Went to the generator, unplugged every wiring harness and plugged back in to make sure it was in properly, and reterminated the utility sense wires at the generator term blocks. Tried to transfer load and continues to do the same thing. Checked to make sure I had 12v on the battery while the generator was not running, and while it was running.
Im at a loss as of what to do next. Could it be something with the display board where all the wiring harnesses go into? It seems to be working properly.
Started looking more in depth and saw I was only getting 2.5vdc from the 12vdc terminal(193) to (0) ground. I was also getting 0v from 193 to to transfer(23). Then I shut the breaker off to try and transfer the load, the generator started, and I got the same readings. If I pull the 12vdc wire off of the SACM board, it then reads 12vdc as it should. As soon as I put it back on the SACM board it drops back to 2.5vdc.
Thought there may have been a short in the wires so I toned them all to make sure I had continuity and also separated them to make sure I was getting no continuity on wires unintentionally. Then thought maybe something was wrong with the SACM so I swapped the whole board and it continued to do the same thing. Went to the generator, unplugged every wiring harness and plugged back in to make sure it was in properly, and reterminated the utility sense wires at the generator term blocks. Tried to transfer load and continues to do the same thing. Checked to make sure I had 12v on the battery while the generator was not running, and while it was running.
Im at a loss as of what to do next. Could it be something with the display board where all the wiring harnesses go into? It seems to be working properly.