I don't have much experience with transfer switches but I think I know what would determine the size of one. If my understanding of this is wrong, please correct me.
Among others, I think the size would be determined by either the load being served or if in the case where the transfer switch is service rated and is being used as the first means of disconnect w/OCP.
What I've run into is a customer that has multiple houses on his property. He has a house, his Mother has a house, and his sister has a house.
He has a 20KW Generac on his house with a 200A ATS. His setup is he has a sub panel with all the circuits in it that are to be backed up. The panel is fed like this:
the POCO (line) side of the ATS is fed from a 100A breaker from one of his main panels
of course the other side from the 20KW generator
the ATS is outside and is fed from the generator and from the panel inside, then back into the house where the backed-up sub panel is.
Since the ATS is not being used as the service and only being supplied 100A from the utility side, and the generator is only a 20KW or 83.33A, I say he only needed a 100A transfer switch.
This discussion came about because he has ask me to connect another generator and ATS to his mother's house. He had mentioned the high cost of the transfer switch on his and I told him he could have used a 100A one. But he said the electrician that installed it told him he had to use a 200A ATS. I told him I was pretty sure he could have just used a 100A.
I think the electrician was confused because the panel feeding it was a 200A panel. But since the ATS wasn't being used as service equipment, or between the meter and his MDP, the 200A was unnecessary.
Am I correct on this?
Among others, I think the size would be determined by either the load being served or if in the case where the transfer switch is service rated and is being used as the first means of disconnect w/OCP.
What I've run into is a customer that has multiple houses on his property. He has a house, his Mother has a house, and his sister has a house.
He has a 20KW Generac on his house with a 200A ATS. His setup is he has a sub panel with all the circuits in it that are to be backed up. The panel is fed like this:
the POCO (line) side of the ATS is fed from a 100A breaker from one of his main panels
of course the other side from the 20KW generator
the ATS is outside and is fed from the generator and from the panel inside, then back into the house where the backed-up sub panel is.
Since the ATS is not being used as the service and only being supplied 100A from the utility side, and the generator is only a 20KW or 83.33A, I say he only needed a 100A transfer switch.
This discussion came about because he has ask me to connect another generator and ATS to his mother's house. He had mentioned the high cost of the transfer switch on his and I told him he could have used a 100A one. But he said the electrician that installed it told him he had to use a 200A ATS. I told him I was pretty sure he could have just used a 100A.
I think the electrician was confused because the panel feeding it was a 200A panel. But since the ATS wasn't being used as service equipment, or between the meter and his MDP, the 200A was unnecessary.
Am I correct on this?