Transfer Switch to Load Center Grounding

Status
Not open for further replies.

erikredd_13

New member
How do you ground a load center to a transfer switch? My utility secondary will run through the utility meter to a manual transfer switch. This is where I will be able to hook up a portable generator or run utility power to my load center.

Do you isolate the neutral and ground to prevent current from running through the ground? Does this work, in a sense, like subfeeding a load center from another load center?

OR

Do you bond your neutral to your ground at your load center?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Welcome to the forum.:)

The answer to this depends on if the generator is a separately derived system. Take a look at 250.35 in the 2008 NEC for grounding requirements for permanently installed generators.

If the neutral in the transfer switch is not switched then the generator would not be a separately derived system and the neutral and equipment grounding conductors of the generator should be kept separate.

Chris
 