transfer switch

Status
Not open for further replies.

mpd

Senior Member
can the upstream breaker protecting a transfer switch, exceed the ampere rating of the transfer switch as long as the transfer switch is sized for the load
 
can the upstream breaker protecting a transfer switch, exceed the ampere rating of the transfer switch as long as the transfer switch is sized for the load

No, it needs to be protected at it's rated ampacity along with the conductors.
 
I was looking at a coordination study that the line side breakers (normal & emergency) were increased from the original design, from what I was told the original design did not coordinate, the plan now shows a 225 amp transfer switch protected by a 400 amp breaker
 
I was looking at a coordination study that the line side breakers (normal & emergency) were increased from the original design, from what I was told the original design did not coordinate, the plan now shows a 225 amp transfer switch protected by a 400 amp breaker

I kind of wondered from your OP if that was the reason you were asking. To be candid, I'm not sure that this is acceptable way to achive selective coordindation as I am only an electrician not an EE. I think there are others here more qualified that hopefully will chime in on this. It is an interesting subject.
 
Last edited:
Just to cover bases, does the transfer switch have any built-in line over-current device ?
 