can the upstream breaker protecting a transfer switch, exceed the ampere rating of the transfer switch as long as the transfer switch is sized for the load
I was looking at a coordination study that the line side breakers (normal & emergency) were increased from the original design, from what I was told the original design did not coordinate, the plan now shows a 225 amp transfer switch protected by a 400 amp breaker
Just to cover bases, does the transfer switch have any built-in line over-current device ?
no the transfer switches have no built in OCP