I am a retired master electrician about to install a generator at my home. Does a double throw double pole disconnect meet the present requirements of NEC?
If the neutral terminal is bonded at the generator the bond must be removed if the neutral is not to be switched. A neutral is connected to the neutral terminal on the generator and a EGC from the existing electrical system must be run and connected to the generator frame. If the neutral is switched the bond is left in place and a ground rod installed and bonded to the generator frame.The neutral can not be switched if the neutral is not bonded at the generator.
If the neutral is bonded at the generator the neutral must be switched.