Transfer Switch
I am a retired master electrician about to install a generator at my home. Does a double throw double pole disconnect meet the present requirements of NEC?
Re: Transfer Switch
As long as the generator neutral is not bonded a simple DPDT manual switch will be OK if you are using it to select the power source for a sub panel.
If you plan on using this switch on the line side of the service disconnect IMO this switch would have to be a service rated switch with overcurrent protection and an off position as it would now be the service disconnect.
Re: Transfer Switch
I'm using it to isolate the incoming power from the generator power so there isn't any feedback onto the main line. The disconnect I'm using is a Cutler-Hammer DT223URK-NPS Double Throw Safety Switch, 100 Amp 240 Volt Three Wire S/N Non-Fusible, Type 3R, Rainproof. My concern is not having the neutral disconnected. Does this meet current NEC standards? The power company says it's okay, but I want to be certain before I install it. I have been out of the business for a few years.
Re: Transfer Switch
The neutral can not be switched if the neutral is not bonded at the generator.
If the neutral is bonded at the generator the neutral must be switched.
I am concerned about your placement of this switch, will there be a service disconnect between this switch and the utility power?
In general no equipment can be on the supply side of the service disconnect. 230.82 lists a few items that are allowed on the supply side of the service disconnect, transfer switches are not one of them.
[ May 24, 2004, 03:23 PM: Message edited by: iwire ]
Re: Transfer Switch
Iwire's I am not sure I have your post clear:
If the neutral terminal is bonded at the generator the bond must be removed if the neutral is not to be switched. A neutral is connected to the neutral terminal on the generator and a EGC from the existing electrical system must be run and connected to the generator frame. If the neutral is switched the bond is left in place and a ground rod installed and bonded to the generator frame.
After reading your post again I think we said the same thing.
Re: Transfer Switch
Sometimes I can not express my self clearly.
Bonded Generator, (SDS) transfer switch must switch the neutral.
No bond at the generator (Non-SDS) do not switch the neutral.
Bob
Re: Transfer Switch
To supplement the excellent advice above, perhaps these sketches may be of some help.
Ed