J jcrider Member Apr 29, 2008 #1 Are disconnecting means or fuse protection required ahead of generator transfer switches ? Code reference ?
Are disconnecting means or fuse protection required ahead of generator transfer switches ? Code reference ?
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor Apr 29, 2008 #2 jcrider said: Are disconnecting means or fuse protection required ahead of generator transfer switches ? Code reference ? Click to expand... Yes, unless the T/S itself is rated as service equipment. Simply put, the main disco must be the first thing hit after the meter. It need not be fused if the service-rated T/S either is OCP'd or the OCPD is immediately adjacent to the service-rated T/S. The code reference is the same as any service requires. The presence of a T/S doesn't change that; you need a service disco.
jcrider said: Are disconnecting means or fuse protection required ahead of generator transfer switches ? Code reference ? Click to expand... Yes, unless the T/S itself is rated as service equipment. Simply put, the main disco must be the first thing hit after the meter. It need not be fused if the service-rated T/S either is OCP'd or the OCPD is immediately adjacent to the service-rated T/S. The code reference is the same as any service requires. The presence of a T/S doesn't change that; you need a service disco.