Can this be done per NEC. I just talked to a customer that had another electricain tell him that if he installed a 200 amp transfer switch between his meter can and main panel It has to be fed from a generator suppling 200 amps. I have not found this in the book anywhere.
The generator the customer has is 25kw. it has a main disconnect sized at 100amps. I believe that as long as the generator suppling it has ocp rated for the wire and generator it would be fine.
Next question . Would the tranfers switch be the first means of disconnect?
Would I have to separate the neutrals and grounds?
I do thank you for this forum.