Transformer 25' Tap rule

Status
Not open for further replies.

brian john

Senior Member
Location
Leesburg, VA
With the 25' tap rule for transformers.

The NEC states (roughly)

Have an ampacity that is at least the value of the primary-to-secondary voltage ratio multiplied by one-third of the rating of the OCPD that protects the primary of the transformer.
Terminate in a single circuit breaker (or set of fuses) rated no more than the secondary conductor ampacity per 310.15 [Table 310.16].
Are protected from physical damage by being enclosed in a manner approved by the AHJ (such as within a raceway).
That first underlined item is throwing me. And I cannot not find consistency in the few online articles I have read or a complete working of the math .

Lets say standard dry type transformer 408 delta-208/120 wye voltage ratio would be 4 to 1 primary to secondary or .25 secondary to primary.

150 KVA transformer, primary OCP 225 Amps, taped with no 3 AWG THHN Copper terminating in a 100 amp FSS with 100 amp fuses.
One showed 480/120, another 120/480, another 480/208 another 208/480?

Is this 4x225=900/3=300 amps? or
Is this .25x225=56.25/3=10.75 amps or
Is this .44x225=99/3=33 amps or
Is this 2.31x225=519/3=173 amps.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The voltage ratio would be 2.31 to 1 for that transfomer. The secondary conductor minimum size for the rule in 240.21(C)(6) would be 225/3(2.31) or 173.25 amps.
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Don, Why 2.31 in lieu of the transformer ratio of 4/1?

The primary voltage is 480V phase-to-phase, the secondary voltage is 208V phase-to-phase. That's a 2.31:1 ratio.

Also consider that the primary rated current is 180.4A and the secondary rated current is 416.4A. That's a 1:2.31 ratio.
 