Transformer above acoustic ceiling tiles

Status
Not open for further replies.

zam

Member
Location
New York, NY
Does the electrical code allow a transformer to be installed above the finished ceiling (above the acoustic ceiling tiles)? Thank you.
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
If it is 50 KVA or less and meets certain conditions, yes.

(B) Hollow Space Installations. Dry-type transformers
1000 volts, nominal, or less and not exceeding 50 kVA shall be
permitted in hollow spaces of buildings not permanently closed
in by structure, provided they meet the ventilation requirements
of 450.9 and separation from combustible materials
requirements of 450.21(A). Transformers so installed shall not
be required to be readily accessible.
 