transformer above suspended cieling

Status
Not open for further replies.
isn't there a limitation to size of transformer above ceiling I thought I have read before you can't put more than 50 kva transformer above ceiling but looking in transformer section I could not find any information
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
isn't there a limitation to size of transformer above ceiling I thought I have read before you can't put more than 50 kva transformer above ceiling but looking in transformer section I could not find any information
Is this what you are looking for? (B)
450.13 Accessibility. All transformers and transformer vaults shall be readily accessible to qualified personnel for inspection and maintenance or shall meet the requirements of 450.13(A) or 450.13(B).

Transformers are not accessible if wiring methods or other equipment obstruct the access of a worker or prevent removal of the covers for inspection or maintenance. Practical clearance considerations required for removal and replacement of the transformer are also important.


(A) Open Installations. Dry-type transformers 600 volts, nominal, or less, located in the open on walls, columns, or structures, shall not be required to be readily accessible.

(B) Hollow Space Installations. Dry-type transformers 600 volts, nominal, or less and not exceeding 50 kVA shall be permitted in hollow spaces of buildings not permanently closed in by structure, provided they meet the ventilation requirements of 450.9 and separation from combustible materials requirements of 450.21(A). Transformers so installed shall not be required to be readily accessible.
 
thank you that is what I was looking for that clears it up I was having a hard time interpreting 450.13 because I thought I had specifically seen suspended ceilings in the terminology I appreciate you taking the time to help
 