Pierre C Belarge
- Westchester County, New York
Thanks Jim, I'm not using secondary OCP since I've protected the primary (208 volt at 125%)
I think I'm getting it although I think there could be a shock hazard if certain conditions were met. As in my post above. I hope I'm wrong.
You most likely found this info in Article 450, That is for protecting the windings, not the conductors.
You are required to have protection on the secondary side, see 240.21(C)and 408.36(D).
This is going to affect the type of circuit breaker you will need. If you are installing this tomorrow, I would call your supply house(s) to see if they have the proper size and type available.