I have a 3-phase pad mounted utility transformer primary rated 13.2KV and 480Y/277 on the secondary. The transformer and the panel serviced are both on the same pad and located about 4 feet apart. The print shows the transformer to be grounded to a 4/0 copper conductor that is installed in the pad, and the print shows to install the three phase conductors and a grounded conductor to the panel, which is be grounded at the panel to the same 4/0 copper conductor the transformer is grounded.
QUESTION: Would this installation violate 250.6, since by grounding both the transformer and the panel to the same grounding electrode, we will be creating a parallel path with the grounded conductor and the grounding electrode system or does the NEC address this type of installation?