Re: Transformer bolted Fault Current
That make sense Jim.
I have always understood that ANSI was a standard that it's intent was to limit fault current but that aspect appeared to have been changed if I read "lile001" reply correctly who said
those standard tables are less than useless. Utilities are moving to lower and lower impedance to improve efficiency
which seemed to contradict what you are saying and what my understanding was. I was also aware that, as you said, transformer designers are able to reduce losses while still maintaining the impedance.
I agree that reducing losses an large transformers is important as the result is significant savings depending upon how the transformer is loaded which can also benefit smaller transformers depending upon how they are loaded.
But back to the 1000kva in question, then what you are saying is that the 5.75%z or greater would still apply?
From my perspective if one ends up with a boarder line KAIC requirement , such a 25.4ka by using an unlimited available fault current on the primary, where you would need to apply 30kaic devices, and you really want to be at 25ka or less you then could consider if is worth you time to identify what the actual available fault current from the utility is as well as fine tuning the impedance figure.
I would like to think that those who do this every day would be able to identify when they would benefit by doing calculations other than the need for documentation in order to justify the ratings and the devices chosen.
I'm a bit out of the main stream and do my best to keep abreast with the changes that are occurring in the industry. That's what I like about this forum. There is a good cross section of knowledge represented which presents many different perspectives.
Thanks,
Dave T