joeyww12000
Senior Member
- Location
- Chatsworth GA
I have noticed on 2 out of 3 jobs Ive been with my company noone bonds there transformers creating seperately derived systems correctly. Yesterday I took the cover off of a step down transformer 480/120-208v because I didnt see a GEC leaving the transformer nor the 120/208v panel it fed, so I became suspicious. I find in the transformer an attempt to bond. I saw a EGC coming in with the feeders tied to a lug that was attached to the case of the xfmr which was fine except there was a bonding jumper from xo and the EGC leaving with the derived phase conductors under that same lug. No the lug was not rated for multiple conductors also there was no GEC anywhere, the system grounded conductor was bonded via the EGC with the xfmr feeders. I know this isnt correct, but theoretically where would the fault current go on a downstream fault on the load side of the xfmr on this setup? Current leaving the xfmr returns to the xfmr, would the egc in with the feeders carry this current if it was of sufficient size....which its not but theoretically?