I have been told by my colleague that my transformer will burn up in the configuration it is, although the facility designer does not think so. I have a 300KVA, 208Y/120Yvolt, 3 phase pad mounted transformer. That equates to 833amps for the transformer rating. I have a 45amp fuse for the primary of the transformer I calculate to be sufficient for this transformer. The primary originates from the substation.
I have two secondaries emanating from this pad mounted transformer; one going to a part of the facility that has a 1200amp fuse in its main circuit breaker. I have another secondary that goes to another part of the facility that has a 800amp fuse in a main switchboard.
My colleague says the two fuses attached to both secondaries add to 2000 amps, i.e. (800amps+1200amps), therefore the transformer will burn up since it is only rated for 800Amps.
It seems to me that the secondary fused at 1200 amps will pull more current than the transformer is rated for provided the load for that secondary exceeds 800amps. This will in fact burn up the transformer in my opinion.
The other secondary is fused at 800amps, which is what the transformer is rated for, so I do not see any connected loads from this secondary causing the transformer to burn up.
Please Advise??
Please Advise??