Hi Guys, Thanks in advance for the replies.
I have a 408/277 service supplying a 30 kva transformer supplying a 208/120 panel in a building which is giving them a 3 phase 100 amp panel basically. They need to add another 3 phase 100 amp panel beside the existing so i see 2 options,
1. Add another 30 kva transformer and duplicate the original installation
2. Take out the original 30 kva install a 75 kva up grade the primary feed and let the original 3 phase 100 stay, then duplicate the original installation for the new 100 amp 3 phase panel.
Any pros cons for the 2 options ? #1 seems to be the logical choice just looking for some advice we never have installed transformers before also for option # 2 can transformers be double tapped on the secondary side ?
My calcs are 30,000 / 480 / 1.732 = 36.08 amps = 40 amp breaker on the primary # 6 cables
30,000 /208 / 1.732 = 83 amps = 90 amp d/c on the secondary # 2 cables
This is what is originally installed although they have a 100 d/c on the secondary.
Any thoughts as i said i am leaning towards Option 1, also the run from transformer to 3 phase 100 amp panel is about 200'
Thanks again for all replys
I have a 408/277 service supplying a 30 kva transformer supplying a 208/120 panel in a building which is giving them a 3 phase 100 amp panel basically. They need to add another 3 phase 100 amp panel beside the existing so i see 2 options,
1. Add another 30 kva transformer and duplicate the original installation
2. Take out the original 30 kva install a 75 kva up grade the primary feed and let the original 3 phase 100 stay, then duplicate the original installation for the new 100 amp 3 phase panel.
Any pros cons for the 2 options ? #1 seems to be the logical choice just looking for some advice we never have installed transformers before also for option # 2 can transformers be double tapped on the secondary side ?
My calcs are 30,000 / 480 / 1.732 = 36.08 amps = 40 amp breaker on the primary # 6 cables
30,000 /208 / 1.732 = 83 amps = 90 amp d/c on the secondary # 2 cables
This is what is originally installed although they have a 100 d/c on the secondary.
Any thoughts as i said i am leaning towards Option 1, also the run from transformer to 3 phase 100 amp panel is about 200'
Thanks again for all replys